G120变频器接地,漏电断路器问题

3347

12

2016-03-30 12:19:35

变频器进线端有一个漏电断路器,进线是三相火线,连接好电机,接好地线,一上电就漏电断路器跳闸。不接地线的话,可以运行的。


不接地线运行的时候,测量地线与变频器的接地端有7到8的交流电压,请问这是正常情况吗?


是不是变频器在正常运行时良好接地的情况下,出现漏电流是正常情况?这样的话,是不是进线前端的漏电断路器是需要去掉的?或是动作电流更大的漏电断路器?


西门子那边给了一个有关使用时漏电断路器的资料,如下:


4.9 Operation with Residual Current Devices (RCD)

If an RCD (also referred to as an ELCB or a RCCB) is fitted, the inverter will operate without nuisance tripping provided that:

● An RCD type B superresistant is used (e.g. a SIQUENCE circuit breaker by Siemens).

● The trip limit of the RCD is 300 mA for filtered units.

● The trip limit of the RCD is 30 mA for unfiltered units.

● The neutral of the supply is grounded.

● Only one inverter is supplied from each RCD.

● The output cables are less than 50 m screened.

If no RCD is used, the touch protection can be achieved by double insulation or by

separating the inverter from the mains system using a transformer.


我们的变频器是没有装进线滤波器的,所以按照说明漏电断路器的动作电流应该30mA,我们线路上的断路器就是30mA。但良好接地就会跳闸


我也看了一些帖子,基本上都说只要PE点良好接地,不需要安装漏电断路器的。


那么,是不是安装漏电断路器是不合理的?但是,去掉的话会有什么危险吗?