| 作者 | 主题 |
|---|---|
|
Auto-Man 游民 经验值:115 发帖数:21 精华帖:0 |
楼主
主题:请版主看看:CPU312 SF灯经常亮!
我的系统硬件组成,PS307 5A;CPU312;2块32点的321;1块32点的322;1块7KFO2;1块4点的AO.
程序中下载了OB1,80,82,85,87,100,121,122 但是CPU经常停机,刚开始的时候,每天要停3,4次,将PS的电断了在重新上电CPU就又好了。后来加了隔离变压器后1周停一次了,也是重新上电就好了。 CPU的诊断信息如下: Diagnostic buffer of module CPU 312 Order No./ Des cription Component Version 6ES7 312-1AE14-0AB0 Hardware 2 - - - Firmware V 3.0.2 Boot Loader Firmware expansion A 25.7.5 Rack: 0 Slot: 2 Event 1 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 09:52:13.118 PM 03/09/2010 Event 2 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 09:52:12.905 PM 03/09/2010 Event 3 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 09:52:12.688 PM 03/09/2010 Event 4 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 09:42:54.702 PM 03/09/2010 Event 5 of 107: Event ID 16# 1382 Request for automatic warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 09:42:54.702 PM 03/09/2010 Event 6 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 09:42:54.620 PM 03/09/2010 Event 7 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 09:42:53.757 PM 03/09/2010 Event 8 of 107: Event ID 16# 494E Power failure Previous operating mode: STOP (internal) Requested operating mode: No voltage External error, Incoming event 09:42:52.616 PM 03/09/2010 Event 9 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 09:42:25.397 PM 03/09/2010 Event 10 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 09:42:25.184 PM 03/09/2010 Event 11 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 09:42:24.967 PM 03/09/2010 Event 12 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 06:47:37.960 PM 03/09/2010 Event 13 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: Power failure Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 06:47:37.960 PM 03/09/2010 Event 14 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: Power failure Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 06:47:37.879 PM 03/09/2010 Event 15 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 06:47:28.655 PM 03/09/2010 Event 16 of 107: Event ID 16# 494E Power failure Previous operating mode: RUN Requested operating mode: No voltage External error, Incoming event 06:47:27.514 PM 03/09/2010 Event 17 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 02:38:27.214 PM 03/09/2010 Event 18 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by stop switch being activated Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 02:38:27.213 PM 03/09/2010 Event 19 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by stop switch being activated Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 02:38:27.132 PM 03/09/2010 Event 20 of 107: Event ID 16# 4303 STOP caused by stop switch being activated Previous operating mode: RUN Requested operating mode: STOP (internal) Incoming event 02:38:25.728 PM 03/09/2010 Event 21 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 04:51:47.184 PM 03/05/2010 Event 22 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 04:51:47.183 PM 03/05/2010 Event 23 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 04:51:47.102 PM 03/05/2010 Event 24 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 04:40:19.139 PM 03/05/2010 Event 25 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 04:40:18.926 PM 03/05/2010 Event 26 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 04:40:18.710 PM 03/05/2010 Event 27 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 04:09:23.698 PM 03/05/2010 Event 28 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 04:09:23.698 PM 03/05/2010 Event 29 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 04:09:23.617 PM 03/05/2010 Event 30 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 05:24:43.709 AM 03/05/2010 Event 31 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 05:24:43.496 AM 03/05/2010 Event 32 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 05:24:43.279 AM 03/05/2010 Event 33 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 02:14:58.667 AM 03/05/2010 Event 34 of 107: Event ID 16# 1382 Request for automatic warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 02:14:58.666 AM 03/05/2010 Event 35 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 02:14:58.586 AM 03/05/2010 Event 36 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 02:14:57.723 AM 03/05/2010 Event 37 of 107: Event ID 16# 494E Power failure Previous operating mode: STOP (internal) Requested operating mode: No voltage External error, Incoming event 02:14:56.582 AM 03/05/2010 Event 38 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 02:14:40.370 AM 03/05/2010 Event 39 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 02:14:40.158 AM 03/05/2010 Event 40 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 02:14:39.941 AM 03/05/2010 Event 41 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 02:07:31.930 AM 03/05/2010 Event 42 of 107: Event ID 16# 1382 Request for automatic warm restart STOP due to: Power failure Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 02:07:31.929 AM 03/05/2010 Event 43 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: Power failure Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 02:07:31.849 AM 03/05/2010 Event 44 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 02:07:30.986 AM 03/05/2010 Event 45 of 107: Event ID 16# 494E Power failure Previous operating mode: RUN Requested operating mode: No voltage External error, Incoming event 02:07:29.853 AM 03/05/2010 Event 46 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 01:35:49.034 AM 03/05/2010 Event 47 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 01:35:49.033 AM 03/05/2010 Event 48 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 01:35:48.952 AM 03/05/2010 Event 49 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 01:34:39.378 AM 03/05/2010 Event 50 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 01:34:39.165 AM 03/05/2010 Event 51 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 01:34:38.948 AM 03/05/2010 Event 52 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 01:06:54.608 AM 03/05/2010 Event 53 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 01:06:54.607 AM 03/05/2010 Event 54 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 01:06:54.527 AM 03/05/2010 Event 55 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 01:06:52.129 AM 03/05/2010 Event 56 of 107: Event ID 16# 494E Power failure Previous operating mode: STOP (internal) Requested operating mode: No voltage External error, Incoming event 01:06:50.996 AM 03/05/2010 Event 57 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 01:00:14.499 AM 03/05/2010 Event 58 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 01:00:14.286 AM 03/05/2010 Event 59 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 01:00:14.069 AM 03/05/2010 Event 60 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 12:26:28.058 AM 03/05/2010 Event 61 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 12:26:28.058 AM 03/05/2010 Event 62 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 12:26:27.976 AM 03/05/2010 Event 63 of 107: Event ID 16# 4358 All modules are ready for operation Operating mode: STOP (internal) Incoming event 11:54:50.159 PM 03/04/2010 Event 64 of 107: Event ID 16# 4357 Module monitoring time started Operating mode: STOP (internal) Incoming event 11:54:49.946 PM 03/04/2010 Event 65 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 11:54:49.730 PM 03/04/2010 Event 66 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered via MPI; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered via MPI; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 10:48:03.720 PM 03/04/2010 Event 67 of 107: Event ID 16# 1381 Request for manual warm restart Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered via MPI; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered via MPI; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 10:48:03.720 PM 03/04/2010 Event 68 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered via MPI; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered via MPI; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 10:48:03.639 PM 03/04/2010 Event 69 of 107: Event ID 16# 5962 Parameter assignment error preventing startup in CPU parameters No relevance for user: SDB:0 Parameter field: MPI parameters Parameter address Byte: 0 , Bit: 0 Error des cription: parameter not in permitted range Operating mode: STOP (memory reset) External error, Incoming event 10:46:29.791 PM 03/04/2010 Event 70 of 107: Event ID 16# 430E Memory reset executed Previous operating mode: STOP (memory reset) Requested operating mode: STOP (own initialization) Incoming event 10:46:29.768 PM 03/04/2010 Event 71 of 107: Event ID 16# 4546 STOP caused by CPU memory management Previous operating mode: STOP (own initialization) Requested operating mode: STOP (memory reset) Internal error, Incoming event 10:46:28.200 PM 03/04/2010 Event 72 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 10:46:28.200 PM 03/04/2010 Event 73 of 107: Event ID 16# 6526 Memory reset request due to memory replacement Operating mode: STOP (own initialization) Internal error, Incoming event 10:46:28.200 PM 03/04/2010 Event 74 of 107: Event ID 16# 494E Power failure Previous operating mode: RUN Requested operating mode: No voltage External error, Incoming event 10:46:27.786 PM 03/04/2010 Event 75 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 06:40:39.701 PM 03/03/2010 Event 76 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 06:40:39.700 PM 03/03/2010 Event 77 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 06:40:39.620 PM 03/03/2010 Event 78 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 03:18:49.978 AM 03/03/2010 Event 79 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 12:06:12.975 AM 03/03/2010 Event 80 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 12:06:12.975 AM 03/03/2010 Event 81 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 12:06:12.895 AM 03/03/2010 Event 82 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 01:04:57.007 AM 03/02/2010 Event 83 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 11:52:27.991 PM 03/01/2010 Event 84 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 11:52:27.990 PM 03/01/2010 Event 85 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 11:52:27.909 PM 03/01/2010 Event 86 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 11:45:39.618 PM 03/01/2010 Event 87 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 10:10:11.606 PM 03/01/2010 Event 88 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 10:10:11.605 PM 03/01/2010 Event 89 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 10:10:11.524 PM 03/01/2010 Event 90 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 10:07:31.855 PM 03/01/2010 Event 91 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 08:45:38.825 PM 03/01/2010 Event 92 of 107: Event ID 16# 1381 Request for manual warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 08:45:38.825 PM 03/01/2010 Event 93 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Warm restart triggered by switch setting; last power on backed up Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Warm restart triggered by switch setting; last power on backed up Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 08:45:38.744 PM 03/01/2010 Event 94 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 11:59:21.596 AM 03/01/2010 Event 95 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 11:20:53.560 PM 02/28/2010 Event 96 of 107: Event ID 16# 1382 Request for automatic warm restart STOP due to: Power failure Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 11:20:53.559 PM 02/28/2010 Event 97 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: Power failure Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 11:20:53.479 PM 02/28/2010 Event 98 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 11:20:52.616 PM 02/28/2010 Event 99 of 107: Event ID 16# 494E Power failure Previous operating mode: RUN Requested operating mode: No voltage External error, Incoming event 11:20:51.564 PM 02/28/2010 Event 100 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 11:19:09.252 PM 02/28/2010 Event 101 of 107: Event ID 16# 1382 Request for automatic warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 11:19:09.252 PM 02/28/2010 Event 102 of 107: Event ID 16# 4301 Mode transition from STOP to STARTUP STOP due to: STOP caused by I/O management Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STOP (internal) Requested operating mode: STARTUP (warm restart) Incoming event 11:19:09.171 PM 02/28/2010 Event 103 of 107: Event ID 16# 4300 Power on backed up Previous operating mode: No voltage Requested operating mode: STOP (own initialization) Incoming event 11:19:08.307 PM 02/28/2010 Event 104 of 107: Event ID 16# 494E Power failure Previous operating mode: STOP (internal) Requested operating mode: No voltage External error, Incoming event 11:19:07.256 PM 02/28/2010 Event 105 of 107: Event ID 16# 4548 STOP caused by I/O management Previous operating mode: RUN Requested operating mode: STOP (internal) Internal error, Incoming event 06:33:52.791 AM 02/27/2010 Event 106 of 107: Event ID 16# 4302 Mode transition from STARTUP to RUN Startup information: - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of automatic startup type at power on: - Automatic warm restart after backed up power on Previous operating mode: STARTUP (warm restart) Requested operating mode: RUN Incoming event 12:54:38.555 AM 02/25/2010 Event 107 of 107: Event ID 16# 1382 Request for automatic warm restart STOP due to: STOP caused by I/O management Startup information: - Startup without modified system configuration - No difference between setpoint and actual configuration - Time for time stamp at the last non backed up power on - Single processor operation Current/last startup type: - Automatic warm restart after backed up power on Permissibility of certain startup types: - Manual warm restart permitted - Automatic warm restart permitted Last valid operation or setting of the automatic startup type at power on: - Automatic warm restart after backed up power on Requested OB: Startup OB (OB100) Priority class: 27 Incoming event 12:54:38.554 AM 02/25/2010 希望版主和高手给予指点。SIEMENS的PLC这次都把我搞的快疯掉了,对siemens产生了动摇。。。。。。 |
|
剑忠 奇侠 经验值:9687 发帖数:622 精华帖:57 |
4楼
主题:回复:请版主看看:CPU312 SF灯经常亮!
1、程序中下载了OB1,80,82,85,87,100,121,122,但怎么没有OB86呢?
2、OB86是用于机架故障(Rack Failure)功能调用的OB块。 3、对于S7-300系列PLC,只需下载OB82、OB86、OB121、OB122这几个组织块至CPU中,就可避免CPU停机(STOP)了。
大学之道,在明明德,在亲民,在止于至善。
|