为何在HW以及NetPro总是来回报错,说一致性检查不能够通过,或者说有冲突什么的?请高手谈点经验!
Error 0x0313: Transmission rate does not match network transmission rate or wrong interrupt
Help on Message 1230:3000
Des cription of Error:
You have saved a configuration which is not consistent. This means no new system data were generated. The configuration was saved correctly.
To Correct or Avoid Error:
If you want to load the configuration the system data must be generated. A correct configuration is a prerequisite for generating the system data.
In some situations, you can use the "Details" button to view details of the cause of the error. System data can be generated once the errors are eliminated.
Outputs for consistency check for E:\Bartell\Program\Siemens\PLC_6_26\PLC 6_26
Outputs for station 'SIMATIC 300(1)':
Error: DP cycle (32.000 ms) has exceeded the maximum value of 8.000 ms for the DP(DRIVE) in PROFIBUS(2)
Result: 1 error(s), 0 warning(s) (08/04/2012 09:49:07 AM)