回复:SU320-2 显示F07930错误

儒雅的小金人

  • 帖子

    610
  • 精华

    5
  • 被关注

    9

论坛等级:侠士

注册时间:2008-07-18

普通 普通 如何晋级?

发布于 2013-02-27 13:07:40

1楼

F07930 Drive: Brake control error
Cause: The Control Unit has detected a brake control error.
Remedy: - check the motor holding brake connection.
- check the function of the motor holding brake.
- check whether there is a DRIVE-CLiQ communication error between the Control Unit and the Motor Module
involved and, if required, carry out a diagnostics routine for the faults identified.
- check that the electrical cabinet design and cable routing are in compliance with EMC regulations (e.g. shield of the
motor cable and brake conductors are connected with the shield connecting plate and the motor connectors are
tightly screwed to the housing).
- replace the Motor Module involved.
Operation with Safe Brake Module:
- check the Safe Brake Modules connection.
- replace the Safe Brake Module.
See also: p1215 (Motor holding brake configuration), p1278 (Brake control, diagnostics evaluation)