quote:以下是引用n次看你的背影在2013-05-16 20:45:27的发言:
呵呵,很抱歉,回来晚了。楼主,你测试过进入光栅、离开光栅后,诊断区故障信息发生的时刻了吗?你看过资料上阀岛输出单元的内部电源原理图了吗?你的安全继电器触点串联在输出单元的总进线电源中还是串联在输出单元的单个回路中?这些都需要你去思考、测试、和确认。我会等待你的反馈信息,以便我们能继续探讨。兄弟,多思考,多测试,多动手有好处!


前辈,你好!我今天做了仔细的测试的(只是摘录了其中某个从站的诊断信息,其他的一样)
一,仅仅断开阀岛输出端(输入端的24VDC此时是接通的),然后重新接通阀岛电源输出端的24VDC电源的时候,CPU只是调用OB82,诊断信息如下:

Event 13 of 200: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Outgoing event
01:39:35.157 PM 05/21/2013

Event 19 of 200: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Distributed I/0s
Input address: 2041
User information available
Diagnostic interrupt from substitute
Module/submodule fault
External module error
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Incoming event
01:39:11.883 PM 05/21/2013


二,断开整个阀岛电源(包括输入端和输出端)的24VDC电源,CPU先调用一次OB86。然后重新接通的时候,CPU再调用一次OB82,OB86。

Event 1 of 200: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 8
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Outgoing event
01:40:06.598 PM 05/21/2013


Event 5 of 200: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Outgoing event
01:40:06.464 PM 05/21/2013

Event 9 of 200: Event ID 16# 39C4
Distributed I/Os: station Failure
Address of the affected DP slave: station number: 8
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Incoming event
01:39:51.175 PM 05/21/2013


最后,安全继电器触点是串联在输出单元的总进线电源中。我目前做了调整,就是保证阀岛的输出端的电源一直有,看看以后会不会再出现问题。如果不出现问题,那就说明阀岛的输出端的24VDC电源被断掉的时候引起了网络问题。

可是,即使最后的实验证明,很有可能是阀岛的输出端的24VDC电源被断掉的时候引起了网络问题。那这是为什么呢???阀岛的输出端只是负责 Q 点的输出,与 I 点无关啊。况且阀岛的输出端的24VDC电源被断掉的时候,CPU的BF指示灯没有报网络故障啊。
拭目以待!谢谢!