问题描述:
上电初始SF灯报红,但只要插入网线与笔记本连接,SF灯消失,程序中有关于以太网通讯的PUT和GET程序块,但还未与其他PLC连接通讯。我想问是不是和PUT和GET程序块有关
诊断如下:
Event 1 of 10: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 2045
Channel information available
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
11:53:17.874 AM 11/02/2013
Event 2 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
11:52:56.783 AM 11/02/2013
Event 3 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
11:52:56.782 AM 11/02/2013
Event 4 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
11:52:56.685 AM 11/02/2013
Event 5 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 8
DP master system ID: 1
Log. base address of the DP slave: Input address: 2039
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:52:56.665 AM 11/02/2013
Event 6 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2035
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:52:56.585 AM 11/02/2013
Event 7 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:52:56.505 AM 11/02/2013
Event 8 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 5
DP master system ID: 1
Log. base address of the DP slave: Input address: 2040
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:52:56.425 AM 11/02/2013
Event 9 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:52:56.367 AM 11/02/2013
Event 10 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Distributed I/0s
Input address: 2045
Channel information available
User information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
11:52:56.321 AM 11/02/2013