德国工程师的最新回复:
the only way is a good shielding of breaking wires and motor power cables. Actually you can not disable break diagnostic with p1278 in Software NC4.5.x. This will be possible from NC4.7.
Sorry, there is no other way around.
If you have further questions don't hesitate to contact me again.
Best regards
Your Technical Support for Industry Automation and Drive Technologies