当抱闸打开时,功率模块的24V电源电压低于21.6V
230054 Power unit: Undervoltage when opening the brake
Message value: %1
Drive object: SERVO, SERVO_SINUMERIK, VECTOR
Reaction: NONE
Acknowledge: NONE
Cause: When the brake is being opened, it is detected that the power supply voltage is less than 24 V - 10% = 21.6V.
Alarm value (r2124, interpret decimal):
Supply voltage fault [0.1 V].
Example:
Alarm value = 212 --> voltage = 21.2 V
Remedy: Check the 24V power supply for stability and value.