414-5H冗余系统,Master CPU启动成功,另外一块CPU无法启动。REDF灯亮,无法同步。但同步光纤之类的都是好的,硬件配置也没有错。因为我们这次有好几组414-5HCPU,拿其他的调试完成的程序和硬件配置灌进去也是一样的故障。
无法启动的CPU的报文如下,求指点:
Event 1 of 120: Event ID 16# 43E7
Standby CPU: Link-up/update by master CPU aborted
Cause: LINK-UP cancelled because the system program in one of the CPUs does not match
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Event occurred in the standby CPU in rack 0
Incoming event
04:40:05.808 PM 05/11/2014
(Coding: 16# 43E7 F044 0050 43D6 0000 0000)
Event 2 of 120: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Event occurred in the master CPU in rack 1
Incoming event
04:40:05.705 PM 05/11/2014
(Coding: 16# 4302 F968 C700 0000 0803 0703)
Event 3 of 120: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by stop switch being activated
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Event occurred in the master CPU in rack 1
Incoming event
04:40:03.037 PM 05/11/2014
(Coding: 16# 4301 F946 C772 4303 0803 0703)
Event 4 of 120: Event ID 16# 43E0
Change from STOP (internal) to link-up mode
STOP due to: STOP caused by stop switch being activated
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Event occurred in the standby CPU in rack 0
Incoming event
04:40:00.583 PM 05/11/2014
(Coding: 16# 43E0 F044 C772 4303 0803 0703)
Event 5 of 120: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting
Operating mode: STOP (internal)
Event occurred in the standby CPU in rack 0
Incoming event
04:40:00.583 PM 05/11/2014
(Coding: 16# 530D F004 C777 0040 0804 0703)
Event 6 of 120: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 3 in rack 0
Number of distributed stations: 13
Event occurred in the standby CPU in rack 0
Incoming event
04:40:00.573 PM 05/11/2014
(Coding: 16# 5371 F003 0050 000D 0000 0000)
Event 7 of 120: Event ID 16# 43F1
Switchover of master CPU and standby CPU
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Event occurred in the standby CPU in rack 1
Incoming event
04:38:55.279 PM 05/11/2014
(Coding: 16# 43F1 F144 0000 0000 0000 0000)
Event 8 of 120: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
- STOP request exists
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Event occurred in the master CPU in rack 0
Incoming event
04:38:30.046 PM 05/11/2014
(Coding: 16# 530D F804 C777 0061 0804 0700)
Event 9 of 120: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
- Module or submodule assignment not evaluated or evaluation aborted with errors (SDB 1,3,5,2X,9X)
- STOP request exists
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI
Permissibility of certain startup types:
- Manual startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Event occurred in the master CPU in rack 0
Incoming event
04:38:29.957 PM 05/11/2014
(Coding: 16# 530D F804 C777 1061 0804 0100)
Event 10 of 120: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
Loading user program or internal inconsistency detected
(SDBs less than 200 incomplete, superfluous, or incorrect)
- Module or submodule assignment not evaluated or evaluation aborted with errors (SDB 1,3,5,2X,9X)
- STOP request exists
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI
Permissibility of certain startup types:
- Manual startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Event occurred in the master CPU in rack 0
Incoming event
04:38:28.073 PM 05/11/2014
(Coding: 16# 530D F804 C777 1161 0804 0100)