CPU是414-2 DP PROFIBUS上一共9个从站,站地址 3.4.5.6.7.9.10.12.20 诊断地址 8187 8189 8188 8187
8186 8181 8184 8179 8182 。
现在的问题是 有时CPU掉线 ,BUS2F指示灯闪烁。重新上线后能正常工作。
用诊断缓冲区诊断后发现OB86机架故障。我把诊断缓冲区的诊断内容发上来请大侠看看
Event 2 of 120: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
12:32:32:972 am 01/01/94
Event 4 of 120: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting
Operating mode: STOP (internal)
Incoming event
12:32:32:943 am 01/01/94
Event 5 of 120: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 9
Priority class: 23
Incoming event
12:32:30:900 am 01/01/94
Event 8 of 120: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
12:32:28:350 am 01/01/94
Event 10 of 120: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Incoming event
12:32:27:384 am 01/01/94
Event 12 of 120: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1000
No relevance for user (Z2): 7fff (Z3): 0608
Previous operating mode: STARTUP (warm restart)
Requested operating mode: STOP (internal)
External error, Incoming event
12:32:21:648 am 01/01/94
Event 13 of 120: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by STOP command
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:32:21:620 am 01/01/94
Event 15 of 120: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
- STOP request exists
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Incoming event
12:32:21:092 am 01/01/94
Event 16 of 120: Event ID 16# 4303
STOP caused by stop switch being activated
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
Incoming event
12:32:21:092 am 01/01/94
Event 17 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 8189
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:29:51:084 am 01/01/94
Event 18 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 12
DP master system ID: 1
Log. base address of the DP slave: Input address: 8179
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:29:28:210 am 01/01/94
Event 19 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 8186
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:29:28:204 am 01/01/94
Event 20 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 10
DP master system ID: 1
Log. base address of the DP slave: Input address: 8184
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:29:28:182 am 01/01/94
Event 21 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 9
DP master system ID: 1
Log. base address of the DP slave: Input address: 8181
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:29:28:097 am 01/01/94
Event 22 of 120: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 10
DP master system ID: 1
Log. base address of the DP slave: Input address: 8184
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
12:29:27:401 am 01/01/94
Event 23 of 120: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 20
DP master system ID: 1
Log. base address of the DP slave: Input address: 8182
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
12:29:25:500 am 01/01/94
Event 24 of 120: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 20
DP master system ID: 1
Log. base address of the DP slave: Input address: 8182
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:29:25:498 am 01/01/94