发布于 2014-06-06 01:00:18
2楼
Event 21 of 114: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
09:15:30.833 AM 06/04/2014
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 22 of 114: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
09:15:30.733 AM 06/04/2014
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 23 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 36
DP master system ID: 1
Log. base address of the DP slave: Input address: 8151
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:15:29.507 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FD7 0124)
Event 24 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 32
DP master system ID: 1
Log. base address of the DP slave: Input address: 8175
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:15:29.428 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FEF 0120)
Event 25 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 30
DP master system ID: 1
Log. base address of the DP slave: Input address: 8176
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:15:29.347 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FF0 011E)
Event 26 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 15
DP master system ID: 1
Log. base address of the DP slave: Input address: 8180
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:15:29.254 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FF4 010F)
Event 27 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 10
DP master system ID: 1
Log. base address of the DP slave: Input address: 8188
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:15:29.098 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FFC 010A)
Event 28 of 114: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8151
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
09:15:29.048 AM 06/04/2014
(Coding: 16# 3842 FE52 C554 1FD7 0063 0000)
Event 29 of 114: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8175
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
09:15:29.047 AM 06/04/2014
(Coding: 16# 3842 FE52 C554 1FEF 0063 0000)
Event 30 of 114: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8176
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
09:15:29.046 AM 06/04/2014
(Coding: 16# 3842 FE52 C554 1FF0 0063 0000)
菜鸟,向大家多学习。