发布于 2014-06-06 01:02:17
9楼
Event 91 of 114: Event ID 16# 2523
Area length error when writing
Global DB, bit access, Access address: 12
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
08:10:41.016 AM 06/04/2014
(Coding: 16# 2523 1B79 0004 000C 0000 0000)
Event 92 of 114: Event ID 16# 253A
DB not loaded
DB number: 1044
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
08:10:41.016 AM 06/04/2014
(Coding: 16# 253A 1B79 007A 0414 0000 0000)
Event 93 of 114: Event ID 16# 2523
Area length error when writing
Global DB, bit access, Access address: 0
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
08:10:41.016 AM 06/04/2014
(Coding: 16# 2523 1B79 0004 0000 0000 0000)
Event 94 of 114: Event ID 16# 253A
DB not loaded
DB number: 1044
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
08:10:41.016 AM 06/04/2014
(Coding: 16# 253A 1B79 007A 0414 0000 0000)
Event 95 of 114: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
08:10:41.016 AM 06/04/2014
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 96 of 114: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
08:10:40.916 AM 06/04/2014
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 97 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 36
DP master system ID: 1
Log. base address of the DP slave: Input address: 8151
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:10:39.671 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FD7 0124)
Event 98 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 32
DP master system ID: 1
Log. base address of the DP slave: Input address: 8175
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:10:39.591 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FEF 0120)
Event 99 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 30
DP master system ID: 1
Log. base address of the DP slave: Input address: 8176
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:10:39.511 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FF0 011E)
Event 100 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 15
DP master system ID: 1
Log. base address of the DP slave: Input address: 8180
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:10:39.431 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FF4 010F)
菜鸟,向大家多学习。