发布于 2014-06-06 01:02:29
10楼
Event 101 of 114: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 10
DP master system ID: 1
Log. base address of the DP slave: Input address: 8188
Log. base address of the DP master: 8191
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:10:39.262 AM 06/04/2014
(Coding: 16# 38C4 FE56 C054 1FFF 1FFC 010A)
Event 102 of 114: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8151
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
08:10:39.214 AM 06/04/2014
(Coding: 16# 3842 FE52 C554 1FD7 0063 0000)
Event 103 of 114: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8175
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
08:10:39.213 AM 06/04/2014
(Coding: 16# 3842 FE52 C554 1FEF 0063 0000)
Event 104 of 114: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8176
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
08:10:39.212 AM 06/04/2014
(Coding: 16# 3842 FE52 C554 1FF0 0063 0000)
Event 105 of 114: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Distributed I/0s
Input address: 8188
User information available
Diagnostic interrupt from substitute
Module/submodule fault
External module error
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
08:10:39.211 AM 06/04/2014
(Coding: 16# 3942 FE52 C554 1FFC 0563 0000)
Event 106 of 114: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 2
Number of distributed stations: 5
Incoming event
08:10:39.210 AM 06/04/2014
(Coding: 16# 5371 FF02 C150 0005 0000 0000)
Event 107 of 114: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
08:10:36.266 AM 06/04/2014
(Coding: 16# 4300 FFF3 0000 0000 0000 0000)
Event 108 of 114: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
06:31:46.596 PM 06/03/2014
(Coding: 16# 494E FF8F C000 0000 0000 0000)
Event 109 of 114: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
09:57:58.772 AM 06/03/2014
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 110 of 114: Event ID 16# 2523
Area length error when writing
Global DB, bit access, Access address: 4
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
09:57:58.768 AM 06/03/2014
(Coding: 16# 2523 1B79 0004 0004 0000 0000)
Event 111 of 114: Event ID 16# 253A
DB not loaded
DB number: 1049
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
09:57:58.768 AM 06/03/2014
(Coding: 16# 253A 1B79 007A 0419 0000 0000)
Event 112 of 114: Event ID 16# 2523
Area length error when writing
Global DB, bit access, Access address: 114
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
09:57:58.768 AM 06/03/2014
(Coding: 16# 2523 1B79 0004 0072 0000 0000)
Event 113 of 114: Event ID 16# 253A
DB not loaded
DB number: 1044
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
09:57:58.768 AM 06/03/2014
(Coding: 16# 253A 1B79 007A 0414 0000 0000)
Event 114 of 114: Event ID 16# 2523
Area length error when writing
Global DB, bit access, Access address: 12
Requested OB: Programming error OB (OB121)
Priority class: 27
Internal error, Incoming event
09:57:58.768 AM 06/03/2014
(Coding: 16# 2523 1B79 0004 000C 0000 0000)
菜鸟,向大家多学习。