给你一个前段时间,处理问题时遇到的CPU暖启动的诊断结果Diagnose.
Diagnostic buffer of module CPU 315-2 DP
Order No./ Des cription Component Version
6ES7 315-2AH14-0AB0 Hardware 4
- - - Firmware V 3.3.8
Boot Loader Firmware expansion A 32.9.9
Rack: 0
Slot: 2
Serial number: S C-****************
Event 1 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
12:09:14.134 AM 08/19/2014
(Coding: 16# 4302 FF68 C700 0000 0810 7710)
Event 2 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
12:09:14.134 AM 08/19/2014
(Coding: 16# 1382 1B64 C772 494E 0810 7710)
Event 3 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:09:14.042 AM 08/19/2014
(Coding: 16# 4301 FF46 C772 494E 0810 7710)
Event 4 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 17
DP master system ID: 1
Log. base address of the DP slave: Input address: 2040
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:09:14.020 AM 08/19/2014
(Coding: 16# 38C4 FE56 C054 07FF 07F8 0111)
注释:暖启动成功后巡站部分较多,不再一一重复!