发布于 2003-01-24 17:56:50
0楼
To set up Ethernet communication, you must fill out the following parameters:
Ethernet Communication Parameters
To Connect from ProSave
1. From the General tab of ProSave, select the correct Device Type (MP370 or MP370 Touch) for your multi panel.
2. From the Connection list box, select Ethernet.
3. Under Connection Parameters, supply the IP Address or Computer Name of the multi panel.
To Connect from ProTool
1. Open the Download Preferences (File > Download > Preferences). The Set Download dialog box opens.
2. Select Ethernet from the list box.
3. Supply the IP Address or Computer Name of the multi panel.
4. (Optional) Select the Enable Upload check box only if you need to be able to upload ProTool projects from the multi panel to the configuration computer.
On the Multi Panel...
Edit Network Configuration
1. From the Control Panel, open the Network Configuration utility.
2. From the Adapters tab, click on the Properties button.
3. Supply an IP address. (This is the IP address referenced in ProTool and ProSave.) * If you obtain an IP address by choosing DHCP, you must restart the multi panel and type ipconfig at the MS-DOS command prompt in order to see what the address is. * If you specify an IP address, you must use one provided by your network administrator if your multi panel is part of an Ethernet network. You can only create your own IP address if your multi panel is not networked, and in that case you must use a crossover cable connection between the multi panel and the configuration computer.
Edit Transfer Settings
1. From the Control Panel, open the Transfer utility.
2. Under Channel 2, select Ethernet from the list box.
3. Select the Enable Channel check box.
Save Your New Settings
1. From the Control Panel, open the OP utility.
2. Click on the Save Registry button to ensure that your configuration will be saved. Otherwise, your settings are reset to the default after the next power cycle.