315-2PN/DP CPU,PN端口LED通讯状态,要求做到HMI上监控。
使用OB82诊断 第一次上电时,明明端口正在通讯,确是错误。好像没有执行OB82,保留的是断电之前的状态。
上电重启会执行OB82吗?
需要在OB100里面先做一下复位吗?
Network1
A(
L #OB82_EV_CLASS
T "PLC_status".EV
SET
SAVE
CLR
A BR
)
JNB _001
L #OB82_FLT_ID
T "PLC_status".FAI
_001: NOP 0
Network2
L #OB82_MDL_ADDR
T "PLC_status".ADD
NOP 0
Network3
L "PLC_status".ADD
L W#16#7FD
==I
= L 20.0
A L 20.0
A(
L DB6.DBW 32
L W#16#3942
==I
)
S "PLC_status".port1_status
A L 20.0
A(
L DB6.DBW 32
L W#16#3842
==I
)
R "PLC_status".port1_status
Network4
L "PLC_status".ADD
L W#16#7FC
==I
= L 20.0
A L 20.0
A(
L DB6.DBW 32
L W#16#3942
==I
)
S "PLC_status".port2_status
A L 20.0
A(
L DB6.DBW 32
L W#16#3842
==I
)
R "PLC_status".port2_status