出现故障时请把CPU故障诊断信息发上来。
哈哈这种问题我遇到过,首先查看CPU诊断信息,判断哪几个DP站掉线,然后从掉线的地方最好加一个中继站,分出两路再进行测试,运行一段时间看看是否会出现掉线。
我当时的情况是:6号,7号,15号站出现掉线,后来加中继站,但是问题没有解决,因为6,7,15号站是一路下来的,然后开始怀疑电源,模块等等有问题,全换了也没能解决问题,最后给6号站从中继站单独走一路,7,15号从中继站走另一路,困扰了我半年的问题总算尘埃落定,那真的大快人心呀。
Diagnostic buffer of module CPU 315F-2PN/DP
Order No./ Description Component Version
6ES7 315-2FJ14-0AB0 Hardware 3
- - - Firmware V 3.2.3
Boot Loader Firmware expansion A 32.9.9
Rack: 0
Slot: 2
Serial number: S C-B4UF40262011
Event 1 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Outgoing event
09:46:32.818 AM 05/26/2014
(Coding: 16# 38C4 1A56 C054 07FF 07FA 0106)
Event 2 of 10: Event ID 16# 79E5
F-I/O passivated
- Monitoring time exceeded at the safety frame detected in the F-CPU
Logical base address: 32
F-I/O database number: 554
External error, Incoming event
09:46:32.625 AM 05/26/2014
(Coding: 16# 79E5 9F00 C47A 022A 0020 0002)
Event 3 of 10: Event ID 16# 39C4
Distributed I/Os: station Failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Incoming event
09:46:32.470 AM 05/26/2014
(Coding: 16# 39C4 1A56 C054 07FF 07FA 0106)
受教了!也恭喜你解决了一件头疼事儿,哈哈