回复:编码器和光栅尺数值不一样会报警吗

gelu172

  • 帖子

    1370
  • 精华

    32
  • 被关注

    170

论坛等级:至圣

注册时间:2010-09-26

黄金 黄金 如何晋级?

发布于 2017-06-09 15:50:06

8楼

 36510  $MA_ENC_DIFF_TOL

Permissible deviation between the actual values of the two measuring systems. This difference must not be exceeded during the cyclic comparison of the two measuring systems used, as otherwise error message 25105 (measuring systems deviate) would be generated.
The corresponding monitoring function is not active
- with MD input value=0,
- if less than 2 measuring systems are active/available in the axis
- or if the axis has not been referenced (at least act. closed-loop control meas. system).
With modulo axes, it is always the absolute value of the shortest/direct position difference that is monitored.

(摘自DoconCD)