我们给客户做的一个项目,300系统的,从17年12月份投入运行,一直正常,到今年五月份开始出现cpu无规律自动停机现象,就是cpu转到stop,重新上电又能运行,到现在越来越频繁,严重时一天一次,客户意见很大。我们更换过接口模块,直流电源,24V电源线重接过,cpu也换了,还是存在问题,怀疑某个模块有问题,但是不能确定哪一个,总不能全部更换。诊断信息也看不出哪个模块有问题,而且输入输出都正常的。OB40/55/80/82/85/86/87/121/122都下载了。
硬件组态如下:
机架0:CPU 315-2dp IM360 321-1BH02一个 321-1FH00一个 322-1HH01六个
机架1:IM361 331-1KF02五个
机架2:IM361 332-5HD01四个
另外DP上有一个DP/MODBUS转换器,下挂八个G120变频器。
导致停机的错误信息如下:
Event 35 of 50: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP due to I/O management
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
02:44:34.130 AM 10/25/2018
(Coding: 16# 1382 1B64 C772 4548 0810 7710)
Event 36 of 50: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP due to I/O management
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:44:34.038 AM 10/25/2018
(Coding: 16# 4301 FF46 C772 4548 0810 7710)
Event 46 of 50: Event ID 16# 4548
STOP due to I/O management
Previous mode: RUN
Requested mode: STOP (internal)
Internal error, Incoming event
02:42:49.587 AM 10/25/2018
(Coding: 16# 4548 FF84 C000 0000 8021 0000)
已经去现场几次了,还是找不到原因,请各位大虾出出注意。