再次发生跳车,检查时,状态指示都恢复正常,没有任何故障灯,诊断记录显示,约3.3s恢复的,请大侠们帮忙分析一下
Event 17 of 3000: Event ID 16# 39B3
I/O access error when updating the process image input table incoming
P area, double-word access, access address: 4
process image partition no.: 2
not user relevant(Z1): 2942
Requested OB: Program execution error OB (OB85)
Priority class: 25
External error, Incoming event
09:28:32.601 AM 09/25/2021
(Coding: 16# 39B3 1955 3050 2942 0200 0004)
Event 18 of 3000: Event ID 16# 39B3
I/O access error when updating the process image input table incoming
P area, double-word access, access address: 0
process image partition no.: 2
not user relevant(Z1): 2942
Requested OB: Program execution error OB (OB85)
Priority class: 25
External error, Incoming event
09:28:32.600 AM 09/25/2021
(Coding: 16# 39B3 1955 3050 2942 0200 0000)
Event 19 of 3000: Event ID 16# 39C4
Distributed I/Os: station Failure
Address of the affected DP slave: station number: 12
DP master system ID: 1
Log. base address of the DP slave: Input address: 16353
Log. base address of the DP master: 16357
Requested OB: Rack failure OB (OB86)
Priority class: 25
External error, Incoming event
09:28:32.590 AM 09/25/2021
(Coding: 16# 39C4 1956 C054 3FE5 3FE1 010C)
Event 20 of 3000: Event ID 16# 5979
Module error in distributed I/O occurred
Slot DP master/IO controller: 8 in rack 0
Event occurred in the master CPU in rack 0
External error, Incoming event
09:28:32.589 AM 09/25/2021
(Coding: 16# 5979 F808 0000 0000 0000 0000)