近期遇到一个问题,PLC出现了死机的问题;
Event 7 of 54: Event ID 16# 4548
STOP due to I/O management
Previous mode: RUN
Requested mode: STOP (internal)
Internal error, Incoming event
06:35:01.908 AM 01/01/1994
(Coding: 16# 4548 FF84 C000 0000 8005 0000)
Event 8 of 54: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 246
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
06:35:01.908 AM 01/01/1994
(Coding: 16# 2942 017A 0020 00F6 0000 0000)
Event 9 of 54: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 244
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
06:35:01.908 AM 01/01/1994
(Coding: 16# 2942 017A 0020 00F4 0000 0000)
Event 10 of 54: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 242
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
06:35:01.908 AM 01/01/1994
(Coding: 16# 2942 017A 0020 00F2 0000 0000)
Event 29 of 54: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 204
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
06:35:01.906 AM 01/01/1994
(Coding: 16# 2942 017A 0020 00CC 0000 0000)
、、、、、、、、、、连续的24个模拟量输入;
Event 30 of 54: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 202
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
06:35:01.906 AM 01/01/1994
(Coding: 16# 2942 017A 0020 00CA 0000 0000)
Event 31 of 54: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 200
Requested OB: I/O access error OB (OB122)
Priority class: 1
External error, Incoming event
06:35:01.905 AM 01/01/1994
(Coding: 16# 2942 017A 0020 00C8 0000 0000)
程序中已调用了OB122;

模拟量的读取采用的是间接寻址方式;本人增加直接访问的一段程序,L PIW200-----L PIW246 ;一直周期内不能两次访问同一个通道吗?