CPU315程序下载后,SF红灯一直亮,看到信息如下,各位高手给看看,程序有何问题?急!!!

已锁定

Darren

  • 帖子

    177
  • 精华

    0
  • 被关注

    3

论坛等级:侠士

注册时间:2003-06-06

普通 普通 如何晋级?

CPU315程序下载后,SF红灯一直亮,看到信息如下,各位高手给看看,程序有何问题?急!!!

645

2

2005-11-28 17:10:48

vent 1 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 100
Module address: 2
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
04:31:42:522 pm 11/28/05


Event 2 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 600
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
04:31:42:522 pm 11/28/05


Event 3 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
04:31:13:545 pm 11/28/05


Event 4 of 100: Event ID 16# 1381
Request for manual warm restart
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
OB not found, or disabled, or cannot be started in the current operating mode
Incoming event
04:31:13:544 pm 11/28/05


Event 5 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
Startup information:
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
04:31:13:462 pm 11/28/05