CPU 412-5H 故障解析求助 冗余、同步故障和trigger event: 43D8

2033

4

2025-06-04 17:43:58

有没有大佬帮忙看下,项目上1台412-5HCPU报警,但是很快又自动恢复了。判断不出故障原因,诊断信息如下:

帮忙看下能否诊断出具体是什么故障引起的,需要更换什么组件。谢谢。


Diagnostic buffer of module CPU 412-5 H PN/DP

Order No./ Description          Component                     Version                      

6ES7 412-5HK06-0AB0                  Hardware                         1                            

- - -                            Firmware                          V 6.0.9                      

Boot Loader                    Firmware expansion               V 6.0.1                      

Rack:                         0

Slot:                           3

Event 1 of 120:  Event ID 16# 7303

H system (1 out of 2) has gone into redundant mode

Occurred in: Master CPU in rack 0

Startup information:

- Startup without modified system configuration

Update time in ms: 390

Requested OB: CPU redundancy error OB (OB72)

Priority class: 28

Incoming event

08:10:17.716 AM  06/03/2025

(Coding: 16# 7303  1C48  CD5B  F808  0000  0186)

 

Event 2 of 120:  Event ID 16# 43E2

Change from update mode to operating mode RUN (redundant mode)

Previous operating mode: UPDATE

Requested operating mode: RUN (redundant mode)

Event occurred in the master CPU in rack 0

Incoming event

08:10:17.701 AM  06/03/2025

(Coding: 16# 43E2  F8C9  0000  0000  0000  0000)

 

Event 3 of 120:  Event ID 16# 43E9

Standby CPU: Change from startup mode to update mode

Previous operating mode: STARTUP (warm restart)

Requested operating mode: UPDATE

Event occurred in the standby CPU in rack 1

Incoming event

08:10:17.110 AM  06/03/2025

(Coding: 16# 43E9  F16C  0000  0000  0000  0000)

 

Event 4 of 120:  Event ID 16# 43E1

Change from link-up mode to update mode

Previous operating mode: LINK-UP

Requested operating mode: UPDATE

Event occurred in the master CPU in rack 0

Incoming event

08:10:17.110 AM  06/03/2025

(Coding: 16# 43E1  F8BC  0000  0000  0000  0000)

 

Event 5 of 120:  Event ID 16# 43E8

Standby CPU: Change from link-up mode to startup mode

STOP due to: Memory reset started automatically (power on not backed up )

Startup information:

- Time for time stamp at the last backed up power on

- Single processor operation

Current/last startup type:

- Automatic warm restart after non backed up power on (with system memory reset)

Permissibility of certain startup types:

- Manual warm restart permitted

Last valid operation or setting of the automatic startup type at power on:

- Automatic warm restart after non backed up power on (with system memory reset)

Previous operating mode: LINK-UP

Requested operating mode: STARTUP (warm restart)

Event occurred in the standby CPU in rack 1

Incoming event

08:10:16.390 AM  06/03/2025

(Coding: 16# 43E8  F1B6  0000  4309  0820  0720)

 

Event 6 of 120:  Event ID 16# 5371

Distributed I/Os: End of the synchronization with a DP master/IO controller   on slot    3 in rack   1

Number of distributed stations:   7

Event occurred in the standby CPU in rack 1

Incoming event

08:10:16.262 AM  06/03/2025

(Coding: 16# 5371  F123  C450  0007  0024  0000)

 

Event 7 of 120:  Event ID 16# 43E0

Change from STOP (internal) to link-up mode

STOP due to: Memory reset started automatically (power on not backed up )

Startup information:

- Time for time stamp at the last backed up power on

- Single processor operation

Current/last startup type:

- Automatic warm restart after non backed up power on (with system memory reset)

Permissibility of certain startup types:

- Manual warm restart permitted

Last valid operation or setting of the automatic startup type at power on:

- Automatic warm restart after non backed up power on (with system memory reset)

Previous operating mode: STOP (internal)

Requested operating mode: LINK-UP

Event occurred in the standby CPU in rack 1

Incoming event

08:10:10.155 AM  06/03/2025

(Coding: 16# 43E0  F14B  C772  4309  0820  0720)

 

Event 8 of 120:  Event ID 16# 43E0

Change from RUN to link-up mode

Previous operating mode: RUN

Requested operating mode: LINK-UP

Event occurred in the master CPU in rack 0

Incoming event

08:10:10.155 AM  06/03/2025

(Coding: 16# 43E0  F88B  0000  0000  0000  0000)

 

Event 9 of 120:  Event ID 16# 3842

Module OK

Module type: Distributed I/0s

Input address:  8116

Channel information available

Alarm in rack 0

Requested OB: Diagnostic interrupt OB (OB82)

OB not found, or disabled, or cannot be started in the in the current operating mode

External error, Outgoing event

08:10:10.051 AM  06/03/2025

(Coding: 16# 3842  FE52  D054  1FB4  0013  0000)

 

Event 10 of 120:  Event ID 16# 3942

Module problem or maintenance necessary

Module type: Distributed I/0s

Input address:  8116

Channel information available

User information available

Module/submodule fault

External module error

Channel error detected

Alarm in rack 0

Requested OB: Diagnostic interrupt OB (OB82)

OB not found, or disabled, or cannot be started in the in the current operating mode

External error, Incoming event

08:10:10.048 AM  06/03/2025

(Coding: 16# 3942  FE52  D054  1FB4  0D33  0000)

 

Event 11 of 120:  Event ID 16# 3942

Module problem or maintenance necessary

Module type: Distributed I/0s

Input address:  8116

Channel information available

User information available

Module/submodule fault

External module error

Channel error detected

Alarm in rack 0

Requested OB: Diagnostic interrupt OB (OB82)

OB not found, or disabled, or cannot be started in the in the current operating mode

External error, Incoming event

08:10:10.046 AM  06/03/2025

(Coding: 16# 3942  FE52  D054  1FB4  0D33  0000)

 

Event 12 of 120:  Event ID 16# 3942

Module problem or maintenance necessary

Module type: Distributed I/0s

Input address:  8116

Channel information available

User information available

Module/submodule fault

External module error

Channel error detected

Alarm in rack 0

Requested OB: Diagnostic interrupt OB (OB82)

OB not found, or disabled, or cannot be started in the in the current operating mode

External error, Incoming event

08:10:04.091 AM  06/03/2025

(Coding: 16# 3942  FE52  D054  1FB4  0D33  0000)

 

Event 13 of 120:  Event ID 16# 45E4

Standby CPU: Change from redundant mode to error-search mode

Error-search mode: trigger event: 43D8: Error-search mode: Hardware error detected due to other error

Previous operating mode: RUN (redundant mode)

Requested operating mode: Error-search mode

Event occurred in the standby CPU in rack 1

Internal error, Incoming event

08:08:58.212 AM  06/03/2025

(Coding: 16# 45E4  F19E  0072  43D8  CACE  0001)

 

Event 14 of 120:  Event ID 16# 43E3

Master CPU: Change from redundant mode to solo mode

Previous operating mode: RUN (redundant mode)

Requested operating mode: RUN

Event occurred in the master CPU in rack 0

Incoming event

08:08:58.212 AM  06/03/2025

(Coding: 16# 43E3  F898  0000  0000  0000  0000)

 

Event 15 of 120:  Event ID 16# 7301

Loss of redundancy (2oo2) due to CPU failure

CPU affected: Standby CPU in rack 1

Requested OB: CPU redundancy error OB (OB72)

Priority class: 28

Incoming event

08:08:58.212 AM  06/03/2025

(Coding: 16# 7301  1C48  005B  F100  0000  0000)


之前诊断信息上传少了一部分。已补全。