有没有大佬帮忙看下,项目上1台412-5HCPU报警,但是很快又自动恢复了。判断不出故障原因,诊断信息如下:
帮忙看下能否诊断出具体是什么故障引起的,需要更换什么组件。谢谢。
Diagnostic buffer of module CPU 412-5 H PN/DP
Order No./ Description Component Version
6ES7 412-5HK06-0AB0 Hardware 1
- - - Firmware V 6.0.9
Boot Loader Firmware expansion V 6.0.1
Rack: 0
Slot: 3
Event 1 of 120: Event ID 16# 7303
H system (1 out of 2) has gone into redundant mode
Occurred in: Master CPU in rack 0
Startup information:
- Startup without modified system configuration
Update time in ms: 390
Requested OB: CPU redundancy error OB (OB72)
Priority class: 28
Incoming event
08:10:17.716 AM 06/03/2025
(Coding: 16# 7303 1C48 CD5B F808 0000 0186)
Event 2 of 120: Event ID 16# 43E2
Change from update mode to operating mode RUN (redundant mode)
Previous operating mode: UPDATE
Requested operating mode: RUN (redundant mode)
Event occurred in the master CPU in rack 0
Incoming event
08:10:17.701 AM 06/03/2025
(Coding: 16# 43E2 F8C9 0000 0000 0000 0000)
Event 3 of 120: Event ID 16# 43E9
Standby CPU: Change from startup mode to update mode
Previous operating mode: STARTUP (warm restart)
Requested operating mode: UPDATE
Event occurred in the standby CPU in rack 1
Incoming event
08:10:17.110 AM 06/03/2025
(Coding: 16# 43E9 F16C 0000 0000 0000 0000)
Event 4 of 120: Event ID 16# 43E1
Change from link-up mode to update mode
Previous operating mode: LINK-UP
Requested operating mode: UPDATE
Event occurred in the master CPU in rack 0
Incoming event
08:10:17.110 AM 06/03/2025
(Coding: 16# 43E1 F8BC 0000 0000 0000 0000)
Event 5 of 120: Event ID 16# 43E8
Standby CPU: Change from link-up mode to startup mode
STOP due to: Memory reset started automatically (power on not backed up )
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after non backed up power on (with system memory reset)
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after non backed up power on (with system memory reset)
Previous operating mode: LINK-UP
Requested operating mode: STARTUP (warm restart)
Event occurred in the standby CPU in rack 1
Incoming event
08:10:16.390 AM 06/03/2025
(Coding: 16# 43E8 F1B6 0000 4309 0820 0720)
Event 6 of 120: Event ID 16# 5371
Distributed I/Os: End of the synchronization with a DP master/IO controller on slot 3 in rack 1
Number of distributed stations: 7
Event occurred in the standby CPU in rack 1
Incoming event
08:10:16.262 AM 06/03/2025
(Coding: 16# 5371 F123 C450 0007 0024 0000)
Event 7 of 120: Event ID 16# 43E0
Change from STOP (internal) to link-up mode
STOP due to: Memory reset started automatically (power on not backed up )
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after non backed up power on (with system memory reset)
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after non backed up power on (with system memory reset)
Previous operating mode: STOP (internal)
Requested operating mode: LINK-UP
Event occurred in the standby CPU in rack 1
Incoming event
08:10:10.155 AM 06/03/2025
(Coding: 16# 43E0 F14B C772 4309 0820 0720)
Event 8 of 120: Event ID 16# 43E0
Change from RUN to link-up mode
Previous operating mode: RUN
Requested operating mode: LINK-UP
Event occurred in the master CPU in rack 0
Incoming event
08:10:10.155 AM 06/03/2025
(Coding: 16# 43E0 F88B 0000 0000 0000 0000)
Event 9 of 120: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 8116
Channel information available
Alarm in rack 0
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
08:10:10.051 AM 06/03/2025
(Coding: 16# 3842 FE52 D054 1FB4 0013 0000)
Event 10 of 120: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Distributed I/0s
Input address: 8116
Channel information available
User information available
Module/submodule fault
External module error
Channel error detected
Alarm in rack 0
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
08:10:10.048 AM 06/03/2025
(Coding: 16# 3942 FE52 D054 1FB4 0D33 0000)
Event 11 of 120: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Distributed I/0s
Input address: 8116
Channel information available
User information available
Module/submodule fault
External module error
Channel error detected
Alarm in rack 0
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
08:10:10.046 AM 06/03/2025
(Coding: 16# 3942 FE52 D054 1FB4 0D33 0000)
Event 12 of 120: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Distributed I/0s
Input address: 8116
Channel information available
User information available
Module/submodule fault
External module error
Channel error detected
Alarm in rack 0
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
08:10:04.091 AM 06/03/2025
(Coding: 16# 3942 FE52 D054 1FB4 0D33 0000)
Event 13 of 120: Event ID 16# 45E4
Standby CPU: Change from redundant mode to error-search mode
Error-search mode: trigger event: 43D8: Error-search mode: Hardware error detected due to other error
Previous operating mode: RUN (redundant mode)
Requested operating mode: Error-search mode
Event occurred in the standby CPU in rack 1
Internal error, Incoming event
08:08:58.212 AM 06/03/2025
(Coding: 16# 45E4 F19E 0072 43D8 CACE 0001)
Event 14 of 120: Event ID 16# 43E3
Master CPU: Change from redundant mode to solo mode
Previous operating mode: RUN (redundant mode)
Requested operating mode: RUN
Event occurred in the master CPU in rack 0
Incoming event
08:08:58.212 AM 06/03/2025
(Coding: 16# 43E3 F898 0000 0000 0000 0000)
Event 15 of 120: Event ID 16# 7301
Loss of redundancy (2oo2) due to CPU failure
CPU affected: Standby CPU in rack 1
Requested OB: CPU redundancy error OB (OB72)
Priority class: 28
Incoming event
08:08:58.212 AM 06/03/2025
(Coding: 16# 7301 1C48 005B F100 0000 0000)
之前诊断信息上传少了一部分。已补全。