注意看这条报警记录:

Event 7 of 120:  Event ID 16# 43E0

Change from STOP (internal) to link-up mode

STOP due to: Memory reset started automatically (power on not backed up )

Startup information:

- Time for time stamp at the last backed up power on

- Single processor operation

Current/last startup type:

- Automatic warm restart after non backed up power on (with system memory reset)

Permissibility of certain startup types:

- Manual warm restart permitted

Last valid operation or setting of the automatic startup type at power on:

- Automatic warm restart after non backed up power on (with system memory reset)

Previous operating mode: STOP (internal)

Requested operating mode: LINK-UP

Event occurred in the standby CPU in rack 1

Incoming event

08:10:10.155 AM  06/03/2025

(Coding: 16# 43E0  F14B  C772  4309  0820  0720)

 

其中有一句话比较重要:

STOP due to: Memory reset started automatically (power on not backed up )

大致意思就是:因为没有电源备份,所以导致 内存自动复位而进入 STOP 模式。

再然后,进入 LINK-UP 模式,与 CPU0 进行同步。同步结束后才会进入 RUN 模式。


我曾经就是通过拿掉保护电池 + 断掉两路电源的方式,让 CPU1 的内存自动复位。然后再上电向 CPU0 进行同步所有数据的(硬件配置、程序等待)。


至于你的 CPU1 为什么会出现这种非人为因素导致程序丢失的情况,只能依靠你自己去查找了。