在线求助:315-2DP重新启动的问题?

已锁定

www123456

西门子1847工业学习平台

  • 帖子

    2379
  • 精华

    87
  • 被关注

    67

论坛等级:至圣

注册时间:2005-09-14

钻石 钻石 如何晋级?

在线求助:315-2DP重新启动的问题?

586

4

2006-12-17 17:11:18

控制柜内315-2DP在工作中有时突然停机(输出点全都停止输出,SF,BF,以及IM360的SF灯全亮),然后PLC自动"重新启动"(表现为RUN灯闪烁到变绿),从停机到重新启动时间极短,有时一天出现几次,不知如何入手?
电源为PS307(5A),它的直流24V能否输出多大电流,是额定5A吗?
外部线路瞬间"短路"能出现这种情况吗?
以下信息看的不太明白,请指教,谢谢!
Diagnostic buffer of module CPU 315-2 DP

Order No./ Des cription Component Version
6ES7 315-2AG10-0AB0 Hardware 4
- - - Firmware V 2.0.10

Rack: 0
Slot: 2


Event 1 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:38:52:020 am 04/29/95


Event 2 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
02:38:52:019 am 04/29/95


Event 3 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:38:51:528 am 04/29/95


Event 4 of 10: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
02:38:39:956 am 04/29/95


Event 5 of 10: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:38:35:785 am 04/29/95


Event 6 of 10: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
12:50:59:956 am 04/29/95


Event 7 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
12:05:31:739 am 04/29/95


Event 8 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
12:05:31:737 am 04/29/95


Event 9 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:05:31:210 am 04/29/95


Event 10 of 10: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
12:05:19:697 am 04/29/95






Diagnostic buffer of module CPU 315-2 DP

Order No./ Des cription Component Version
6ES7 315-2AG10-0AB0 Hardware 4
- - - Firmware V 2.0.10

Rack: 0
Slot: 2


Event 1 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:38:52:020 am 04/29/95


Event 2 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
02:38:52:019 am 04/29/95


Event 3 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:38:51:528 am 04/29/95


Event 4 of 10: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
02:38:39:956 am 04/29/95


Event 5 of 10: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:38:35:785 am 04/29/95


Event 6 of 10: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
12:50:59:956 am 04/29/95


Event 7 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
12:05:31:739 am 04/29/95


Event 8 of 10: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
12:05:31:737 am 04/29/95


Event 9 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
12:05:31:210 am 04/29/95


Event 10 of 10: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
12:05:19:697 am 04/29/95




在线求助:315-2DP重新启动的问题? 已锁定
编辑推荐: 关闭

请填写推广理由:

本版热门话题

SIMATIC S7-300/400

共有54616条技术帖

相关推荐

热门标签

相关帖子推荐

guzhang

恭喜,你发布的帖子

评为精华帖!

快扫描右侧二维码晒一晒吧!

再发帖或跟帖交流2条,就能晋升VIP啦!开启更多专属权限!

  • 分享

  • 只看
    楼主

top
您收到0封站内信:
×
×
信息提示
很抱歉!您所访问的页面不存在,或网址发生了变化,请稍后再试。