这段诊断信息包含了些什么内容?应该怎么处理?

已锁定

我是工控大臭

  • 帖子

    510
  • 精华

    1
  • 被关注

    4

论坛等级:侠客

注册时间:2003-06-06

普通 普通 如何晋级?

这段诊断信息包含了些什么内容?应该怎么处理?

792

7

2007-01-29 13:58:40

Diagnostic buffer of module CPU 315-2 DP

Order No./ Des cription Component Version
6ES7 315-2AG10-0AB0 Hardware 3
- - - Firmware V 2.0.5

Rack: 0
Slot: 2


Event 1 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:55:38:126 am 12/09/06


Event 2 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
OB number: 1
Module address: 3204
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
11:55:37:801 am 12/09/06


Event 3 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:55:37:865 am 12/09/06


Event 4 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 280
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
11:55:37:781 am 12/09/06


Event 5 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Incoming event
11:55:37:780 am 12/09/06


Event 6 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:57:19:820 pm 11/24/06


Event 7 of 100: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
02:57:19:818 pm 11/24/06


Event 8 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:57:18:946 pm 11/24/06


Event 9 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
10:57:27:357 am 11/24/06


Event 10 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
10:57:27:281 am 11/24/06


Event 11 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
10:57:27:207 am 11/24/06


Event 12 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
10:55:46:599 am 11/24/06


Event 13 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
10:55:46:528 am 11/24/06


Event 14 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
10:55:43:408 am 11/24/06


Event 15 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
10:52:11:807 am 11/24/06


Event 16 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
OB number: 1
Module address: 3204
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
10:52:11:553 am 11/24/06


Event 17 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
10:52:11:576 am 11/24/06


Event 18 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 280
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
10:52:11:539 am 11/24/06


Event 19 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Incoming event
10:52:11:535 am 11/24/06


Event 20 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:40:54:456 pm 11/20/06


Event 21 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: Power failure
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
02:40:54:455 pm 11/20/06


Event 22 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: Power failure
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:40:53:692 pm 11/20/06


Event 23 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:823 pm 11/20/06


Event 24 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:733 pm 11/20/06


Event 25 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 5
DP master system ID: 1
Log. base address of the DP slave: Input address: 2043
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:660 pm 11/20/06


Event 26 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 2044
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:554 pm 11/20/06


Event 27 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:492 pm 11/20/06


Event 28 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:404 pm 11/20/06


Event 29 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2043
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:402 pm 11/20/06


Event 30 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2044
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:400 pm 11/20/06


Event 31 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:40:42:396 pm 11/20/06


Event 32 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 5
Incoming event
02:40:42:387 pm 11/20/06


Event 33 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:40:27:862 pm 11/20/06


Event 34 of 100: Event ID 16# 494E
Power failure
Previous operating mode: RUN
Requested operating mode: No voltage
External error, Incoming event
02:40:11:695 pm 11/20/06


Event 35 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:32:46:025 pm 11/20/06


Event 36 of 100: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:32:46:023 pm 11/20/06


Event 37 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:32:45:262 pm 11/20/06


Event 38 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 2044
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:37:16:610 pm 08/28/06


Event 39 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2044
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
12:37:16:535 pm 08/28/06


Event 40 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 2044
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
12:37:11:267 pm 08/28/06


Event 41 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:56:262 am 08/07/06


Event 42 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:56:199 am 08/07/06


Event 43 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:26:56:160 am 08/07/06


Event 44 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:49:298 am 08/07/06


Event 45 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:49:227 am 08/07/06


Event 46 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:26:49:130 am 08/07/06


Event 47 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:32:856 am 08/07/06


Event 48 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:32:786 am 08/07/06


Event 49 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:26:32:708 am 08/07/06


Event 50 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:15:409 am 08/07/06


Event 51 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:15:338 am 08/07/06


Event 52 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:26:15:308 am 08/07/06


Event 53 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:05:176 am 08/07/06


Event 54 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:26:05:073 am 08/07/06


Event 55 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:26:02:722 am 08/07/06


Event 56 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:26:02:623 am 08/07/06


Event 57 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:09:10:909 am 07/30/06


Event 58 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
08:09:10:803 am 07/30/06


Event 59 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:31:09:061 am 07/26/06


Event 60 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:31:09:005 am 07/26/06


Event 61 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
02:31:08:942 am 07/26/06


Event 62 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:43:26:024 am 07/05/06


Event 63 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:43:25:955 am 07/05/06


Event 64 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:43:25:895 am 07/05/06


Event 65 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:43:15:247 am 07/05/06


Event 66 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:43:15:187 am 07/05/06


Event 67 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:43:15:077 am 07/05/06


Event 68 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 2044
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:43:01:310 am 07/05/06


Event 69 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2044
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:43:01:242 am 07/05/06


Event 70 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 2044
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:43:01:202 am 07/05/06


Event 71 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:58:617 am 07/05/06


Event 72 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:58:549 am 07/05/06


Event 73 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:58:495 am 07/05/06


Event 74 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:57:409 am 07/05/06


Event 75 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:57:302 am 07/05/06


Event 76 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:41:504 am 07/05/06


Event 77 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:41:435 am 07/05/06


Event 78 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:41:369 am 07/05/06


Event 79 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:38:505 am 07/05/06


Event 80 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2041
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:38:445 am 07/05/06


Event 81 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 2041
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:38:361 am 07/05/06


Event 82 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:32:750 am 07/05/06


Event 83 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:32:679 am 07/05/06


Event 84 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:32:628 am 07/05/06


Event 85 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:25:817 am 07/05/06


Event 86 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:25:746 am 07/05/06


Event 87 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:25:700 am 07/05/06


Event 88 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:13:169 am 07/05/06


Event 89 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
09:42:13:095 am 07/05/06


Event 90 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
09:42:13:061 am 07/05/06


Event 91 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
01:11:44:402 am 07/04/06


Event 92 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
01:11:44:296 am 07/04/06


Event 93 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
05:26:26:746 am 06/24/06


Event 94 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
05:26:26:675 am 06/24/06


Event 95 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
05:26:26:592 am 06/24/06


Event 96 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:14:06:021 am 05/28/06


Event 97 of 100: Event ID 16# 3842
Module OK
Module type: DP standard slave
Input address: 2042
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
08:14:05:946 am 05/28/06


Event 98 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
08:14:05:910 am 05/28/06


Event 99 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
03:23:46:597 am 05/24/06


Event 100 of 100: Event ID 16# 39C4
Distributed I/Os: station failure
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2046
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
03:23:46:495 am 05/24/06


这段诊断信息包含了些什么内容?应该怎么处理? 已锁定
编辑推荐: 关闭

请填写推广理由:

本版热门话题

SIMATIC S7-300/400

共有54759条技术帖

相关推荐

热门标签

相关帖子推荐

guzhang

恭喜,你发布的帖子

评为精华帖!

快扫描右侧二维码晒一晒吧!

再发帖或跟帖交流2条,就能晋升VIP啦!开启更多专属权限!

  • 分享

  • 只看
    楼主

top
X 图片
您收到0封站内信:
×
×
信息提示
很抱歉!您所访问的页面不存在,或网址发生了变化,请稍后再试。