下面是根据你的使用的实际情况选择哪种自动重启的说明:另外建议你在使用软件如starter/Drivemonitor时使用帮助功能,很有好处的
P1210 = 0:
Automatic restart is disabled.
P1210 = 1:
The inverter will acknowledge (reset) faults i.e. it will reset a
fault when the is re-applied. This means the inverter must be fully
powered down, a brownout is not sufficed. The inverter will not run
until the ON command has been toggled.
P1210 = 2:
The inverter will acknowledge the fault F0003 at power on after
blackout and restarts the drive. It is necessary that the ON command
is wired via digital input (DIN).
P1210 = 3:
For these settings it is fundamental that the drive only restarts if
it has been in a RUN state at the time of the faults (F0003, etc.).
The inverter will acknowledge the fault and restarts the drive after
a blackout or bronwout. It is necessary that the ON command is wired
via digital input (DIN).
P1210 = 4:
For these settings it is fundamental that the drive only restarts if
it has been in a RUN state at the time of the fault (F0003). The
inverter will acknowledge the fault and restarts the drive after a
blackout or bronwout. It is necessary that the ON command is wired
via digital input (DIN).
P1210 = 5:
The inverter will acknowledge the faults F0003 etc. at power on after
blackout and restarts the drive. It is necessary that the ON command is wired via digital input (DIN).
P1210 = 6:
The inverter will acknowledge the faults (F0003 etc.) at power on
after blackout or brownout and restarts the drive. It is necessary
that the ON command is wired via digital input (DIN). Setting 6 causes the motor to restart immediately.