我公司一台设备用的是西门子313CPU,今天在运行过程中出现CPU自动停止情况,此时CPU上SF,STOP点亮,然后设备再次启动即可,可是3小时左右又重复出现该故障,下面是CPU诊断信息:Diagnostic buffer of module CPU 313C-2 DP
Order No./ Des cription Component Version
6ES7 313-6CF03-0AB0 Hardware 1
- - - Firmware V 2.0.12
Rack: 0
Slot: 2
Event 1 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
11:58:00.439 PM 02/24/1995
Event 2 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
11:57:59.972 PM 02/24/1995
Event 3 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
11:57:59.958 PM 02/24/1995
Event 4 of 100: Event ID 16# 39C4
Distributed I/Os: station Ausfall
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
Priority class: 26
External error, Incoming event
11:57:59.953 PM 02/24/1995
Event 5 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
02:08:55.935 PM 02/24/1995
Event 6 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
02:08:55.934 PM 02/24/1995
Event 7 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
02:08:54.933 PM 02/24/1995
Event 8 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 1018
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:08:54.551 PM 02/24/1995
Event 9 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 1019
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:08:54.444 PM 02/24/1995
Event 10 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 5
DP master system ID: 1
Log. base address of the DP slave: Input address: 1020
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:08:54.372 PM 02/24/1995
Event 11 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 1022
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:08:54.264 PM 02/24/1995
Event 12 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 32767
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:08:54.174 PM 02/24/1995
Event 13 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1019
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:08:53.869 PM 02/24/1995
Event 14 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1020
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:08:53.867 PM 02/24/1995
Event 15 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1022
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:08:53.864 PM 02/24/1995
Event 16 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1018
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:08:53.861 PM 02/24/1995
Event 17 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 5
Incoming event
02:08:53.842 PM 02/24/1995
Event 18 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
02:08:50.342 PM 02/24/1995
Event 19 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
02:08:25.520 PM 02/24/1995
Event 20 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:02:30.260 PM 02/24/1995
Event 21 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 1022
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:02:29.986 PM 02/24/1995
Event 22 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 7
DP master system ID: 1
Log. base address of the DP slave: Input address: 1018
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:02:29.895 PM 02/24/1995
Event 23 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 5
DP master system ID: 1
Log. base address of the DP slave: Input address: 1020
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:02:29.809 PM 02/24/1995
Event 24 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1022
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:02:29.756 PM 02/24/1995
Event 25 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1018
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:02:29.747 PM 02/24/1995
Event 26 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1020
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:02:29.741 PM 02/24/1995
Event 27 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 1019
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
02:02:13.190 PM 02/24/1995
Event 28 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1019
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
02:02:13.131 PM 02/24/1995
Event 29 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:58:48.611 PM 02/24/1995
Event 30 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:58:48.601 PM 02/24/1995
Event 31 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:58:48.574 PM 02/24/1995
Event 32 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:58:48.573 PM 02/24/1995
Event 33 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:58:48.090 PM 02/24/1995
Event 34 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:58:36.711 PM 02/24/1995
Event 35 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:58:22.393 PM 02/24/1995
Event 36 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:51:01.604 PM 02/24/1995
Event 37 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:50:26.449 PM 02/24/1995
Event 38 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:50:26.439 PM 02/24/1995
Event 39 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:50:26.405 PM 02/24/1995
Event 40 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:50:26.404 PM 02/24/1995
Event 41 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:50:25.924 PM 02/24/1995
Event 42 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:50:14.534 PM 02/24/1995
Event 43 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:50:00.232 PM 02/24/1995
Event 44 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:49:42.444 PM 02/24/1995
Event 45 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:47:36.218 PM 02/24/1995
Event 46 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:47:36.209 PM 02/24/1995
Event 47 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:47:36.177 PM 02/24/1995
Event 48 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:47:36.176 PM 02/24/1995
Event 49 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:47:35.695 PM 02/24/1995
Event 50 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:47:24.282 PM 02/24/1995
Event 51 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:47:09.948 PM 02/24/1995
Event 52 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:47:00.160 PM 02/24/1995
Event 53 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:46:57.343 PM 02/24/1995
Event 54 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:46:57.334 PM 02/24/1995
Event 55 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:46:57.306 PM 02/24/1995
Event 56 of 100: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:46:57.305 PM 02/24/1995
Event 57 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered by switch setting; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered by switch setting; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:46:56.817 PM 02/24/1995
Event 58 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:46:30.793 PM 02/24/1995
Event 59 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:46:30.783 PM 02/24/1995
Event 60 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:46:30.748 PM 02/24/1995
Event 61 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:46:30.747 PM 02/24/1995
Event 62 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:46:30.267 PM 02/24/1995
Event 63 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:46:18.876 PM 02/24/1995
Event 64 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:46:04.574 PM 02/24/1995
Event 65 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:27:21.786 PM 02/24/1995
Event 66 of 100: Event ID 16# 39C4
Distributed I/Os: station Ausfall
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 1019
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
01:27:13.072 PM 02/24/1995
Event 67 of 100: Event ID 16# 39C4
Distributed I/Os: station Ausfall
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 1022
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
01:27:13.064 PM 02/24/1995
Event 68 of 100: Event ID 16# 39C4
Distributed I/Os: station Ausfall
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
01:27:13.059 PM 02/24/1995
Event 69 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 4
DP master system ID: 1
Log. base address of the DP slave: Input address: 1022
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
01:27:13.029 PM 02/24/1995
Event 70 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1018
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
01:27:12.974 PM 02/24/1995
Event 71 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1020
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
01:27:12.971 PM 02/24/1995
Event 72 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1022
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
01:27:12.964 PM 02/24/1995
Event 73 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
01:27:12.912 PM 02/24/1995
Event 74 of 100: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 6
DP master system ID: 1
Log. base address of the DP slave: Input address: 1019
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
01:27:10.093 PM 02/24/1995
Event 75 of 100: Event ID 16# 3842
Module OK
Module type: Distributed I/0s
Input address: 1019
User information available
Diagnostic interrupt from substitute
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Outgoing event
01:27:10.035 PM 02/24/1995
Event 76 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:26:56.194 PM 02/24/1995
Event 77 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:26:56.184 PM 02/24/1995
Event 78 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:26:56.156 PM 02/24/1995
Event 79 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:26:56.155 PM 02/24/1995
Event 80 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:26:55.674 PM 02/24/1995
Event 81 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:26:44.284 PM 02/24/1995
Event 82 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:26:29.981 PM 02/24/1995
Event 83 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:26:00.193 PM 02/24/1995
Event 84 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:25:02.113 PM 02/24/1995
Event 85 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:25:02.103 PM 02/24/1995
Event 86 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:25:02.069 PM 02/24/1995
Event 87 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:25:02.068 PM 02/24/1995
Event 88 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:25:01.588 PM 02/24/1995
Event 89 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:24:50.198 PM 02/24/1995
Event 90 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:24:35.896 PM 02/24/1995
Event 91 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:09:51.106 PM 02/24/1995
Event 92 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:05:08.292 PM 02/24/1995
Event 93 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
01:05:08.282 PM 02/24/1995
Event 94 of 100: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
01:05:08.254 PM 02/24/1995
Event 95 of 100: Event ID 16# 1382
Request for automatic warm restart
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Startup with modified system configuration
- Difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
01:05:08.253 PM 02/24/1995
Event 96 of 100: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Automatic warm restart after backed up power on
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic warm restart permitted
Last valid operation or setting of the automatic startup type at power on:
- Automatic warm restart after backed up power on
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
01:05:07.770 PM 02/24/1995
Event 97 of 100: Event ID 16# 5371
Distributed I/Os: end of the synchronization with a DP master
Slot of the DP master: 2
Number of distributed stations: 0
Incoming event
01:04:56.391 PM 02/24/1995
Event 98 of 100: Event ID 16# 4300
Power on backed up
Previous operating mode: No voltage
Requested operating mode: STOP (own initialization)
Incoming event
01:04:42.057 PM 02/24/1995
Event 99 of 100: Event ID 16# 494E
Power failure
Previous operating mode: STOP (internal)
Requested operating mode: No voltage
External error, Incoming event
01:04:17.267 PM 02/24/1995
Event 100 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2318
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
01:04:07.957 PM 02/24/1995
我在程序块中添加了OB86,OB122,OB82块,可是还是不行,望斑竹和路过的大侠赐教!谢谢!