cpu414-2dp,带一个ET200分站和47个电机综保(电机综保以分站形式挂接在profibus总线上),ET200分站通信正常,有四个电机综保通信不上其他电机综保通信正常,cpu上EXTF灯亮,BUSF2灯闪烁;cpu以这种状态运行一周后也就是昨天突然cpu上所有的灯都开始一起闪烁了,编程电脑与cpu不能通信,将cpu断电再上电并打到stop状态,电脑用编程适配器与 cpu 连接读取诊断buffer里的信息如下:
Diagnostic buffer of module CPU 414-2 DP
Order No./ Des cription Component Version
6ES7 414-2XG03-0AB0 Hardware 5
- - - Firmware V 3.0.0
Rack: 0
Slot:
Event 1 of 100: Event ID 16# 49A0
STOP caused by parameter assignment error or unpermissible difference between preset and actual configuration: startup disabled
No relevance for user (SDB no.): 1
No relevance for user (Z2): 7fff (Z3): 000c
Previous operating mode: STOP (internal)
Requested operating mode: STOP (internal)
External error, Incoming event
05:31:22:437 pm 07/24/04
Event 2 of 100: Event ID 16# 5962
Parameter assignment error preventing startup in CPU module parameters
Parameter: free
Error type: unable to generate a default parameter record
Operating mode: STOP (internal)
External error, Incoming event
05:31:22:437 pm 07/24/04
Event 3 of 100: Event ID 16# 530D
New startup information in STOP mode
Startup prevented by:
- STOP request exists
- Keyswitch set to STOP
- Cold restart or warm restart necessary
Startup information:
- Time for time stamp at the last non backed up power on
- Single processor operation
Current/last startup type:
- No startup type/following memory reset
Permissibility of certain startup types:
- Manual warm restart permitted
Last valid operation or setting of automatic startup type at power on:
- No startup type/following memory reset
Operating mode: STOP (internal)
Incoming event
05:31:22:421 pm 07/24/04
Event 4 of 100: Event ID 16# 430E
Memory reset executed
Initialization information: Memory reset due to inconsistent data
Previous operating mode: STOP (memory reset)
Requested operating mode: STOP (own initialization)
Incoming event
05:31:19:782 pm 07/24/04
Event 5 of 100: Event ID 16# 4309
Memory reset started automatically (power on not backed up )
Initialization information: Memory reset due to inconsistent data
No relevance for user (Z1): 0001
Previous operating mode: No voltage
Requested operating mode: STOP (memory reset)
Incoming event
05:31:19:729 pm 07/24/04
Event 6 of 100: Event ID 16# 4550
DEFECTIVE: internal system error
No relevance for user (Z1): b715
No relevance for user (Z2): 8f02 (Z3): 0205
Previous operating mode: RUN
Requested operating mode: DEFECTIVE
Internal error, Incoming event
07:06:04:728 pm 07/23/04
Event 7 of 100: Event ID 16# 39B1
I/O access error when updating the process image input table
P area, double-word access, access address: 151
process image partition no.: 0
not user relevant(Z1): 2942
Requested OB: Program execution error OB (OB85)
Priority class: 25
External error, Incoming event
07:06:04:727 pm 07/23/04
其中事件1~5是cpu断电再上电后产生的,事件6是导致cpu上所有登闪烁的原因,事件7以后的是综保没通上信导致的。
以前没遇见过这种现象,请教各位仁兄,为何CPU上所有灯在闪烁,该如何解决才能至少不让cpu停止。拜托了!