回复:急!S120系统电源模块SLM(36KW)内部的继电器开关在自检后不闭合,启动总报警F30003,F7490

天枰

  • 帖子

    315
  • 精华

    10
  • 被关注

    15

论坛等级:侠士

注册时间:2007-08-09

普通 普通 如何晋级?

发布于 2011-02-27 10:47:24

8楼

F07490 switch on inhibit 合闸禁止,可能你的配置没有完成或不正确,检查r0002的值
Values:
0: [00] Operation - everything enabled
21: [21] Ready for operation - set "Operation enable" = "1" (p0852)
31: [31] Ready for switching on - power-up operation running (r3402)
32: [32] Ready for switching on - set "ON/OFF1" = "0/1" (p0840)
41: [41] Switching on inhibited - set "ON/OFF1" = "0" (p0840)
42: [42] Switching on inhibited - set "OC/OFF2" = "1" (p0844, p0845)
45: [45] Switch on inhibit - remove fault cause, acknowledge fault
46: [46] Switching on inhibited - exit comm mode (p0009, p0010)
47: [47] Switching on inhibited - refer to r46
60: [60] Infeed de-activated
85: [85] Test mode active (p6650)
250: [250] Device signals a topology error

F30003 说明你的整流部分没有工作
DP灯常亮,说明DP通讯正常,能够正确识别模块
RDY灯绿色闪烁(好像1S闪1次),Rreen/Red Flashing ligth 0.5Hz CU320 is ready for operation,however there are no software licenese