哪个大哥帮忙看看,诊断信息

已锁定

seaaide

  • 帖子

    76
  • 精华

    0
  • 被关注

    5

论坛等级:游侠

注册时间:2008-02-14

普通 普通 如何晋级?

哪个大哥帮忙看看,诊断信息

1196

3

2011-05-09 19:54:20

315 2pn/dp,电脑走pn口
sm321+3个sm322
后面是rs485 is coupler,再后面是et200isp的站

今天只下载硬件组态,程序只有空的OB1,OB81,OB82,OB84,OB86等等

两个问题
a) 在硬件组态中强制DO,模块灯不亮(今天来不及撤查接线,只量了公共端电压)
b) cpu和et200isp都亮sf灯,诊断信息中提示的OB无法下载,提示优先级错误,但是在线却看到相应的OB在cpu中,请问是什么造成这些OB不起作用的?


Diagnostic buffer of module CPU 315-2PN/DP

Order No./ Des cription Component Version
6ES7 315-2EH14-0AB0 Hardware 2
- - - Firmware V 3.1.1
Boot Loader Firmware expansion A 26.7.7

Rack: 0
Slot: 2


Serial number: S C-ANVN02112010


Event 1 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Digital SM with bit granular address area
Input address: 0
Channel information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Incoming event
07:03:27.729 AM 01/01/1994


Event 2 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Digital SM with bit granular address area
Input address: 0
Channel information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Incoming event
07:03:27.708 AM 01/01/1994


Event 3 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Digital SM with bit granular address area
Input address: 0
Channel information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Incoming event
07:03:27.577 AM 01/01/1994


Event 4 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Digital SM with bit granular address area
Input address: 0
Channel information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
Priority class: 26
External error, Incoming event
07:03:27.552 AM 01/01/1994


Event 5 of 10: Event ID 16# 4302
Mode transition from STARTUP to RUN
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STARTUP (warm restart)
Requested operating mode: RUN
Incoming event
07:01:13.692 AM 01/01/1994


Event 6 of 10: Event ID 16# 1381
Request for manual warm restart
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Startup without modified system configuration
- No difference between setpoint and actual configuration
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Requested OB: Startup OB (OB100)
Priority class: 27
Incoming event
07:01:13.689 AM 01/01/1994


Event 7 of 10: Event ID 16# 4301
Mode transition from STOP to STARTUP
STOP due to: STOP caused by PG stop operation or by SFB 20 "STOP"
Startup information:
- Time for time stamp at the last backed up power on
- Single processor operation
Current/last startup type:
- Warm restart triggered via MPI; last power on backed up
Permissibility of certain startup types:
- Manual warm restart permitted
- Automatic startup not permitted, corrections in parameter assignment, submodule, etc. necessary
Last valid operation or setting of the automatic startup type at power on:
- Warm restart triggered via MPI; last power on backed up
Previous operating mode: STOP (internal)
Requested operating mode: STARTUP (warm restart)
Incoming event
07:01:13.543 AM 01/01/1994


Event 8 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 3
DP master system ID: 1
Log. base address of the DP slave: Input address: 2040
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
07:01:13.536 AM 01/01/1994


Event 9 of 10: Event ID 16# 38C4
Distributed I/Os: station return
Address of the affected DP slave: station number: 2
DP master system ID: 1
Log. base address of the DP slave: Input address: 2042
Log. base address of the DP master: 2047
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Outgoing event
07:01:12.416 AM 01/01/1994


Event 10 of 10: Event ID 16# 3942
Module problem or maintenance necessary
Module type: Digital SM with bit granular address area
Input address: 36
Channel information available
Module/submodule fault
External module error
Channel error detected
Requested OB: Diagnostic interrupt OB (OB82)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
07:01:11.474 AM 01/01/1994