s7-300系统一棘手问题

1843

10

2011-08-08 19:37:16

我公司一台设备用的是S7-300系统,有313CPU,321,322,331,153等常见模块,还有一TP170A触摸屏,profibus网络上有CPU,153,TP170A,还有4台MM440变频器,昨天工人在电焊作业时,没把设备断电,导致设备触摸屏TP170A被烧,还有明显的模拟量模块331被烧,并且固定模块的西门子DIN导轨上有明显电击痕迹,最初故障表现是153站、331模块红灯闪,CPU的SF,BF灯亮,后来将其换掉后,网络正常,CPU正常,现在设备能正常运行,但是奇怪的是运行一段时间后CPU就会自动进入STOP状态,并且CPU上SF灯亮,打开STEP7,在线监视CPU,出现报警,信息如下:Diagnostic buffer of module CPU 313C-2 DP

Order No./ Des cription Component Version
6ES7 313-6CF03-0AB0 Hardware 1
- - - Firmware V 2.6.1
Boot Loader Firmware expansion A 0.21.0

Rack: 0
Slot: 2


Event 1 of 100: Event ID 16# 39C4
Distributed I/Os: station Ausfall
Address of the affected DP slave: station number: 1
DP master system ID: 1
Log. base address of the DP slave: Input address: 1016
Log. base address of the DP master: 1023
Requested OB: Rack failure OB (OB86)
OB not found, or disabled, or cannot be started in the current operating mode
External error, Incoming event
Event 2 of 100: Event ID 16# 4563
STOP caused by I/O access error (OB not loaded or not possible, or no FRB)
Breakpoint in user program: Cyclic program (OB1)
Priority class: 1
FC number: 1
Module address: 2344
Previous operating mode: RUN
Requested operating mode: STOP (internal)
Internal error, Incoming event
Event 3 of 100: Event ID 16# 2942
I/O access error, reading
P area, word access, Access address: 292
Requested OB: I/O access error OB (OB122)
OB not found, or disabled, or cannot be started in the in the current operating mode
External error, Incoming event
不知何故?并且CPU中添加了一空的OB86,还是不可以,还望路过的朋友赐教!先谢谢了