周一来了一个有经验的师傅给装上了。
一)recommissioning the control panel
1:switch the isolating swith on
2:simultaneously press and keep depressed the MAIN MENU key and first thress softkey (面板上的左侧三个白键)。
3:press the NC-ON key with these keys depressed :the whole memory area of the control panel is now cleared.
4:the CRT is cleared and apperas:no system data available carry out commissioning.
二)selecting and cancelling the system data input operating mode
1:when after re-start the picture "no system date"appears. input code-wort "SYSDAT" directhy.
the picture appears on the CRT ,than the system data can now be entered.
另(三)commissioning of siemens 3t with index c200
1:pc1 ram memoryclear 关机-后面灰色4开关拨到stop-开机-nc on-5开关(restart)按下并保持,此时红灯亮,按一下9按钮(reset),红灯和绿灯亮,最后剩红灯亮-放开5按钮-将4拨上(run),红灯和绿灯亮,最后红灯亮-按一下9按钮,绿灯亮。-关机。
2:nc1 clear(te data memory)将拨码由0拨到1,8保护开关拨到上面。-开机。C200基本画面会出现。
安装步骤看的不是太清楚,具体还要看实际情况。