Diagnostic buffer of module CPU 414-4 H
Order No./ Des cription Component Version
6ES7 414-4HJ04-0AB0 Hardware 1
- - - Firmware V 4.0.10
Rack: 0
Slot: 3
Event 95 of 100: Event ID 16# 45E4
Standby CPU: Change from redundant mode to error-search mode
Error-search mode: trigger event: 4533: Checksum error
Event: ###404###ANZEIGETEXTECPU=
OB number: Multicomputing interrupt OB (OB60)
Priority class: 0
Previous operating mode: RUN (redundant mode)
Requested operating mode: Error-search mode
Event occurred in the standby CPU in rack 0
Internal error, Incoming event
04:42:31:206 pm 11/10/11
Event 96 of 100: Event ID 16# 43E3
Master CPU: Change from redundant mode to solo mode
Previous operating mode: RUN (redundant mode)
Requested operating mode: RUN
Event occurred in the master CPU in rack 1
Incoming event
04:42:31:205 pm 11/10/11
Event 97 of 100: Event ID 16# 7301
Loss of redundancy (2oo2) due to CPU failure
CPU affected: Standby CPU in rack 0
Event: Standby CPU: Change from redundant mode to error-search mode
Requested OB: CPU redundancy error OB (OB72)
Priority class: 28
Incoming event
04:42:31:205 pm 11/10/11
Event 98 of 100: Event ID 16# 7303
H system (1 out of 2) has gone into redundant mode
Occurred in: Master CPU in rack 1
Startup information:
- Startup without modified system configuration
Update time in ms: 91
Requested OB: CPU redundancy error OB (OB72)
Priority class: 28
Incoming event
04:41:37:040 pm 11/10/11
Event 99 of 100: Event ID 16# 43E2
Change from update mode to operating mode RUN (redundant mode)
Previous operating mode: UPDATE
Requested operating mode: RUN (redundant mode)
Event occurred in the master CPU in rack 1
Incoming event
04:41:37:011 pm 11/10/11
Event 100 of 100: Event ID 16# 43E9
Standby CPU: Change from startup mode to update mode
Previous operating mode: STARTUP (warm restart)
Requested operating mode: UPDATE
Event occurred in the standby CPU in rack 0
Incoming event
04:41:36:689 pm 11/10/11