QUESTION 4 : 31X型PLC插入MMC卡后,STOP灯不停闪烁,怎么办? 或 如何格式化MMC?
Why does the STOP LED flash on my CPU 31xC when the MMC (Micro Memory Card) is slotted? The CPU does not behave like this with other MMCs.
ANSWER:
The MMC in your CPU is not formatted or contains data that cannot be interpreted by this CPU (e.g. the configuration of a different CPU type or an operating system not compatible with the CPU).
WARNING:
When you format the MMC all the data that is located on the MMC is deleted!
Proceed as follows to format the MMC.
1. Your CPU requests an overall reset (slow flashing of the STOP LED).
2. Put the switch into the MRES position and hold it there until the STOP LED lights permanently (approx. 9 seconds).
3. You must then release the switch within the next 3 seconds and then put it back into the MRES position. The STOP-LED now flashes during formatting.
If the MMC cannot be formatted as described above, then the MMC is defective.
NOTE:
It is only possible to format the MMC if there is data located on the MMC that is invalid for the CPU. Otherwise the MMC is only initialized through the steps described.
More information on the MMC is available in Entry ID: 8861901


在网络课堂的300/400分类中有mmc资料的下载。
网络课堂是个好地方,大家可以多去看看,希望西门子不断的更新内容
http://www.ad.siemens.com.cn/service/e-training/
课堂地址
评论
编辑推荐: 关闭

请填写推广理由:

本版热门话题

SIMATIC S7-300/400

共有54706条技术帖

相关推荐

热门标签

相关帖子推荐

guzhang

恭喜,你发布的帖子

评为精华帖!

快扫描右侧二维码晒一晒吧!

再发帖或跟帖交流2条,就能晋升VIP啦!开启更多专属权限!

  • 分享

  • 只看
    楼主

top
X 图片
您收到0封站内信:
×
×
信息提示
很抱歉!您所访问的页面不存在,或网址发生了变化,请稍后再试。